Services & Support
Application Center
  Application Center
How do I work on the parameter settings when using the servo drive ASDA-A2 series with the human machine controller HMC series?

Confirm the setting and servo drive version:

-Setup P3-00 for servo drive station number. In DMCNet, it must have station 1..

Setup P1-01 in control mode of servo drive:

When set P1-01= x00b, the drive is using DMCNET

Setup P3-01 for drive communication:

-For general servo drive, set P3-01 = 0203

-For 4-axis synchronous control drive, set P3-01= 5203

How to clear the alarm of servo drive:

-Servo drive’s alarm reset, set 【FAULT RESET】(R592, R593, R594, …) to ON

-Make sure【SERVO FAULT】(R1104, R1105, R1106, …) is set to OFF

-Make sure【SERVO WARNING】(R1120, R1121, R1122, …) is set to OFF

How to activate servo

-The servo axis that executes motion has to be activated. Set【Servo On】(R576, R577, R578,…) to On.

-Make sure the servo drive is On. Set 【Servo On】(R1072, R1073, R1074,…) to On.

Release Quick Stop

-【Quick stop】(R528, R529, R530,…) of the servo axis that executes motion hasto be Off.

-Make sure the quick stop status of the servo drive is released. Set【Servo quickstop release】(R1088, R1089, R1090, …) to On.

-If the quick stop status cannot be released, please check the DI setting of the servo drive.


-When it is not in Handwheel status, make sure 【Handwheel activate】(R608, R609, R610, …) is set to Off.
  FAQ Center Menu
Please Select

RSS Feeds
Press Releases
Privacy Contact us
Terms of use  
© 2018 Delta Electronics, Inc. All Rights Reserved.